CARI Infonet

 Forgot password?
 Register

ADVERTISEMENT

Author: geima

MASALAH PENDAWAIAN ELEKTRIK

[Copy link]
Post time 18-1-2019 05:42 PM From the mobile phone | Show all posts
KILL_NANCY replied at 18-1-2019 08:19 AM
waalaikumsalam ketpo.

lampu apa catpaw boleh saya tahu?fluorescent ke?confirm ke bulb fused?dah ...

Lampu macam ni. Ada starterkah lampu macam ni? yang kalimantang tu saya tau tukar starter. yang jenis ni tak tau pula

This post contains more resources

You have to Login for download or view attachment(s). No Account? Register

x
Reply

Use magic Report


ADVERTISEMENT


Post time 19-1-2019 12:10 AM From the mobile phone | Show all posts
Catpaw replied at 18-1-2019 05:42 PM
Lampu macam ni. Ada starterkah lampu macam ni? yang kalimantang tu saya tau tukar starter. yang je ...

ahaha cakaplah energy saving atau cfl bulb.watt yang sama?samada ballast malfunction atau terminal dalam holder tu dah bent.ada orang lelaki tak dalam rumah?adik ke?
Reply

Use magic Report

Post time 19-1-2019 08:24 AM From the mobile phone | Show all posts
Edited by Catpaw at 19-1-2019 08:25 AM
KILL_NANCY replied at 19-1-2019 12:10 AM
ahaha cakaplah energy saving atau cfl bulb.watt yang sama?samada ballast malfunction atau terminal ...


rumah sewa laki tak dibenarkan masuk, kang ada yg ngamuk

Kitorang nak cuba tukar sendiri dulu, kalau tak jadi baru nak panggil org dtg buat... hari tu tanya kedai dia cakap rm25 tukar dalam tu utk satu katanya...
Reply

Use magic Report

Post time 19-1-2019 06:59 PM From the mobile phone | Show all posts
Catpaw replied at 19-1-2019 08:24 AM
rumah sewa laki tak dibenarkan masuk, kang ada yg ngamuk  

Kitorang nak cuba tukar  ...

ohhh.ingatkan tinggal dengan adik2.

hati2.jangan ON switch.takut ballast malfunction.kemungkinan terminal kat holder bent tu pun ada.
Reply

Use magic Report

Post time 7-4-2019 02:09 AM From the mobile phone | Show all posts
Assalamualaikum otai2 letrikal....
Nak tanya, setiap kali saya on aircond, tak kira lah aircond di hall atau di bilik, lampu2 di dalam rumah pasti berkedip sekali.
Tekan on sahaja di remote, lampu rumah berkedip. Kenapa ye? Adakah ini tanda2 litar pintas?

Rate

1

View Rating Log

Reply

Use magic Report

Post time 7-4-2019 02:33 AM | Show all posts
kena panggil otai @KILL_NANCY  utk jawap
Reply

Use magic Report

Follow Us
Post time 7-4-2019 04:48 AM From the mobile phone | Show all posts
AyongKhamsiah replied at 7-4-2019 02:09 AM
Assalamualaikum otai2 letrikal....
Nak tanya, setiap kali saya on aircond, tak kira lah aircond di  ...

waalaikumsalam ayong.

bila selalu jadi?siang atau malam atau tak kira waktu?

macam ni.lampu flicker ni tak semestinya bersangkut paut dengan short circuit atau ia tidak semestinya terdapat masalah dalam pendawaian.selalunya itu hanyalah heavy load pada arus elektrik awak dan mungkin itu hanya temporarily current tu nak reduce the amount of electricity maksud saya yang sedia ada seperti lampu dan peralatan elektrik lain di rumah awak tu.

kemungkinan :


1 . apabila lampu berkelip atau flicker tu maksudnya voltage dah dropped.kalau rumah awak pakai mentol jenis incandescent (yang ada tungsten wire kat dalam tu) memang sensitif dan cepat berkelip.kalau awak pakai mentol CFL (compact fluorescent lamp/energy saving light) atau mentol LED dia kurang berkelip dan tidak terlalu sensitif.

voltage yang dropped tu sebabnya large current draw maksudnya ia berlaku hanya sementara waktu apabila compressor air cond startup atau dalam keadaan hidup <<<< masa ni compressor run sebelum 75% daya fluks) dan itu normal.

mungkin saya cadangkan untuk penambahan aksesori air cond seperti pemasangan soft stater.fungsinya adalah untuk kurangkan pengaliran arus elektrik ketika air cond dalam keadaan startup atau hidup .


Single Phase Soft Stater


2 . tapi harus diingat, kalau large current draw tu terlalu lama, breaker awak akan trip.JUGA, jika lampu tu tak berhenti berkelip dan berkelip secara constant selepas compressor startup KEMUNGKINAN, air cond awak ada masalah kerosakan kipas pada compressor (outdoor unit) yang boleh menyebabkan air cond jadi bising atau wujud vibrations. <<<< ni kena panggil technician atau sebelum tu awak boleh dengar sendiri outdoor unit samada bising atau tidak.

3 . check mcb punya kapasiti berapa amp digunakan.check sekali elcb yang awak guna samada 40A/63A dengan kadar sensitiviti 30 hingga 100mA untuk domestik.mungkin juga saiz kabel yang tak ikut specs atau piawaian yang ditetapkan oleh ST, atau kabel awak injured disebabkan oleh gigitan haiwan atau kabel dah mula longkah, dah start mereput.ni semua boleh menyumbang kepada lampu jadi flicker/berkelip.

kesimpulan :


apa pun awak perlu pastikan bahawa kelipan hanya berlaku apabila air cond dihidupkan.samada kelipan tu hanya sementara atau constant.

bila awak ON je air cond, motor compressor akan mula berfungsi dan menggunakan lebih kurang 100+ amps untuk beberapa saat pertama (locked rotor amps) iaitu sebelum 75% daya fluks.tenaga yang digunakan adalah jauh lebih besar daripada full load amps!!! <<<< misal kata air cond awak 2 horsepower dengan voltage yang digunakan 220v, full load amps pun baru 10A.jauh beza ya.

sebaik sahaja motor compressor melepasi daya fluks tersebut, arus akan decrease to a much lesser value, iaitu lebih kurang 2 hingga ke 5 amps.

harap membantu.

Rate

1

View Rating Log

Reply

Use magic Report

Post time 7-4-2019 04:49 AM From the mobile phone | Show all posts
ip_lepat replied at 7-4-2019 02:33 AM
kena panggil otai @KILL_NANCY  utk jawap

haha mana ada otai bang.biasa2 je.average je saya ni.
Reply

Use magic Report


ADVERTISEMENT


Post time 7-4-2019 02:31 PM | Show all posts
KILL_NANCY replied at 7-4-2019 04:49 AM
haha mana ada otai bang.biasa2 je.average je saya ni.

tima kasih bang
kima dah rate tu
Reply

Use magic Report

Post time 18-4-2019 01:29 PM From the mobile phone | Show all posts
As'salam

Aku skang ni chargeman A1 dan bekerja kat sebuah company ni company construction memang buat kerja kerja letrik..So skang aku memang lemah bab pengiraan letrik ada budak budak kat sini yang higher qualification dr aku pon tak bole jawab bila aku tanya..Aku nak tau mcm mana pengiraan

- carry line 33kv

- rating transformer 1000kva

- 11kv primary current

- 415v secondary current

- ACB size

Ni kat HT/LV room..Aku hrp ada otai otai letrik kat sini sudi bantu..Urgent case ni sbb bulan depan kami nak start kerja kerja pemasangan kat sebuah bangunan area selangor..Bangunan baru..Trimas

Rate

1

View Rating Log

Reply

Use magic Report

Post time 18-4-2019 04:49 PM | Show all posts
KILL_NANCY replied at 7-4-2019 04:49 AM
haha mana ada otai bang.biasa2 je.average je saya ni.

Mod, bantuan diperlukan utk jawapan post diatas
Terima kasih
Reply

Use magic Report

Post time 18-4-2019 09:40 PM | Show all posts
MdAli replied at 18-4-2019 01:29 PM
As'salam

Aku skang ni chargeman A1 dan bekerja kat sebuah company ni company construction memang  ...

assalam, ada orang suruh pass jawapan

CALCULATION 33KV / 11KV CARRY LINE                                 


If details are :                                                                  

V            : 415                                                         
PF         : 0.9                                                         
CT KVA : 1000                                                         

FORMULAE         

KW : KVA X PF                                                                 
KW : 1000 X 0.9                                                                 
KW : 900                                                                 

11KV PRIMARY CURRENT                                         

KW : Root (3) X KV X I X PF                                                                 
900 : 1.732 X 11 X I X 0.9                                                                 
900 : 17.1468 X I                                                                 
900/17.1468 : I                                                                 
52.49         : I                                                         
I         : 52.49A                        

415V SECONDARY CURRENT                                         

WATTS : Root (3) X V X I X PF                                                                 
900 X 1000 : 1.732 X 415 X I X 0.9                                                                 
900000         : 646.90 X I                                                         
900000/646.9 : I                 
1391.3         : I                                                         
I         : 1391.3A         

RATING OF TRANSFORMER 1000 KVA                                         

        Primary Voltages on High Voltages sided is : 11KV                                                         
        Primary Current on High Voltage i : 52.49A

        Secondary Voltages on Low Voltages sided is : 415V                                                         
        Secondary Current on Low Voltage is : 1391.3A         

        Transformer rating in KVA : 1000KVA                                                         
        Primary Voltages : 11KV                                                         
        Primary Current : 52.49A                                                         
        Secondary Voltages : 415V                                                         
        Secondary Current : 1391.3A                          

CALCULATION FOR THE RATING OF TRANSFORMER ACCORDING TO :                                                         

        P : V X I (Primary Voltage X Primary Current)                                                         
        P : 11000V X 52.49A = 577390VA = 577.39KVA                                                         

AND                                                

        P : V X I (Secondary Voltage X Secondary Current)                                                         
        P : 415V X 1391.3A = 577390VA = 577.39KVA                                                                       
        P : Root (3) X V X I                    

        P : Root (3) X Primary Voltage X Primary Current                                                         
        P : 1.732 X 11000V X 52.49A = 1000039.48VA = 1000 KVA [CHECKED]                                                                       
        P : Root (3) X Secondary Voltage X Secondary Current                                                         
        P : 1.732 X 415V X 1391.3A = 1000038.6VA = 1000 KVA [CHECKED]

RATING OF THE THREE PHASE TRANSFORMER                                         

        Voltage (line to line)                         : 208V                                 
        Current (line current)                         : 1391.3A                                 

        P : Root (3) X V X I                                                         
        P : 1.732 X 208V X1391.3A                                                         
        P : 501224.2VA                                                         
        P : 501 KVA / 500 KVA                                                         


ABBREVIATIONS                 

PF         : Power Factor                                                         
I         : Amperage                                                         
KV         : Kilo Volt                                                         
KW         : Kilo Watt                                                         
V         : Volt                                                         
KVA : Kilo Volt Ampere                                                         
CT         : Current Transformer                                                         
P         : Power                                                         
VA         : Voltage Ampere                                       






Rate

1

View Rating Log

Reply

Use magic Report

Post time 19-4-2019 09:17 AM From the mobile phone | Show all posts
MeghanK replied at 18-4-2019 09:40 PM
assalam, ada orang suruh pass jawapan

CALCULATION 33KV / 11KV CARRY LINE                     ...

TQ Tuan sgt detail..1391.3A tue ACB rate kan? Aku bab kira kira mmg lemah sikit..Bagos la forum ni aku tanya kat fb org tak layan aku..Mesti level BO ni incas aku kalu tanya je blur blur nk jwb abis kuat pon suh goggle hihihi.. Tinggal mn tuan jum kita lepaking minum minum ke aku bdk meru..
Reply

Use magic Report

Post time 20-4-2019 11:54 AM From the mobile phone | Show all posts
MdAli replied at 19-4-2019 09:17 AM
TQ Tuan sgt detail..1391.3A tue ACB rate kan? Aku bab kira kira mmg lemah sikit..Bagos la forum ni ...

nanti tunggu tukang bagi jawapan @KILL_NANCY masuk jawabkan..dia outstation skang ni
Reply

Use magic Report

Post time 26-4-2019 04:57 PM | Show all posts
Assalamualaikum,

saya ada pertanyaan pada otai2,

Rumah saya ada dua bilik dan satu tandas yang menggunakan satu MCB 6Amp yang sama, point yang asal ada 3, satu untuk setiap bilik dan satu lagi untuk tandas.(Point di Siling)

boleh ke saya loop kan, supaya setiap bilik ada 1 point untuk kipas dan 2 point untuk lampu LED downlight 12w. tandas kekal dengan 1 point lampu.

jadi nya beban yang akan ditanggung oleh MCB 6amp ni adalah;
-2 kipas
-5 lampu downlight

Rumah  saya wiring standard lagi,

Terima kasih

Rate

1

View Rating Log

Reply

Use magic Report

Post time 27-4-2019 09:53 PM From the mobile phone | Show all posts
sham13 replied at 26-4-2019 04:57 PM
Assalamualaikum,

saya ada pertanyaan pada otai2,


hai sham13

basic sangat ni.

sebelum tu saya assume rumah sham pakai single phase lah ya.

untuk miniature circuit breaker atau mcb 6A dengan ketebalan kabel 1.5mm boleh carry 10 biji mata lampu + kipas atau total connected load (tlc) tidak lebih 1kW.

jadi jawapannya dibenarkan.

sham boleh kira sendiri faktor kepelbagaian bagi kipas dan lampu.

untuk lampu, ni formulanya :

NOS x watts / volts x 1.8 (amplicity correction factor) x 66%

jom kira Amps lampu sham.

5 x 12w / 240v x 1.8 x 66% = 0.287A

formula kipas pula :

(NOS x watts/volts x 0.85) x 66%

(2 x 65w / 240v x 0.85) x 66% = 0.4206A

jumlah permintaan arus = 0.7076A

harap membantu ....



Comments

Mod, terima kasih  Post time 27-4-2019 10:29 PM

Rate

2

View Rating Log

Reply

Use magic Report


ADVERTISEMENT


Post time 28-4-2019 10:02 AM From the mobile phone | Show all posts
wahhhh kredit melimpah ruah.thanks mod semua.
Reply

Use magic Report

Post time 22-5-2019 06:54 PM | Show all posts
Salam..nk ty sket, basic question je kot pd sifoo...knp ye tetiba lampu malap kjp2 utk 1 rmh, tp bende lain mcm kipas ok je..fius dkt DB nk rosak ke hapa??harap dpt jawap soalan sy ni haa ye..
Reply

Use magic Report

Post time 23-5-2019 10:43 PM | Show all posts
KILL_NANCY replied at 28-4-2019 10:02 AM
wahhhh kredit melimpah ruah.thanks mod semua.

beb, free kalu tolong jwp post kat atas
TQ
Reply

Use magic Report

Post time 7-6-2019 01:06 PM From the mobile phone | Show all posts
salam, rumah saye ni tetibe lampu malap, kipas jadi slow, tv takleh bukak, peti ais lampu aje menyala. ape agaknye malasalah?
Reply

Use magic Report

You have to log in before you can reply Login | Register

Points Rules

 

ADVERTISEMENT



 

ADVERTISEMENT


 


ADVERTISEMENT
Follow Us

ADVERTISEMENT


Mobile|Archiver|Mobile*default|About Us|CARI Infonet

26-4-2024 03:24 PM GMT+8 , Processed in 0.155385 second(s), 45 queries .

Powered by Discuz! X3.4

Copyright © 2001-2021, Tencent Cloud.

Quick Reply To Top Return to the list